  • #1880

    TArnett
    Keymaster

    Hello. Are there any members (besides Plains End) that have Unitrol 1000 AVR’s installed on your generators? If so how are you meeting the NERC standard for PSS monitoring and reporting?

    #1881

    Jeremy Saar
    Participant

    On the AVR, scroll to setup and then scroll down to PSS. When you hit OK if PSS is active it will show PSS Active = True.

    You can either take a picture of that or log it.

     

    #1920

    KMoore
    Participant

    Due to requirements in ERCOT (TRE) we were required to upgrade to the Unitrol 1020… So we have a spare 1000 if anyone needs it. Additionally, we had Wartsila add a visual indicator on the engine control page for each engine that shows AVR in Auto and PSS Active. We pulled these points into PI and can run a trend.

Viewing 3 posts - 1 through 3 (of 3 total)